On Tue, Nov 01, 2011 at 06:19:36AM -0400, Jean Delvare wrote: > The NCT6775F and NCT6776F have specific temperature sensor resolutions > for sensors above 3. > > Signed-off-by: Jean Delvare <khali@xxxxxxxxxxxx> > Cc: Guenter Roeck <guenter.roeck@xxxxxxxxxxxx> > --- > Guenter, did I get it right? > Did I add the 0.0 degrees note ? Brr. Anyway, it is kind of correct. temp7 to temp9 resolution is 0.5 degrees C, but the code only reads full degrees because it was too complicated to merge the lowest bit. Acked-by: Guenter Roeck <guenter.roeck@xxxxxxxxxxxx> Thanks, Guenter > Documentation/hwmon/w83627ehf | 5 +++-- > 1 file changed, 3 insertions(+), 2 deletions(-) > > --- linux-3.2-rc0.orig/Documentation/hwmon/w83627ehf 2011-10-31 17:00:50.000000000 +0100 > +++ linux-3.2-rc0/Documentation/hwmon/w83627ehf 2011-11-01 10:55:03.000000000 +0100 > @@ -62,8 +62,9 @@ sensors. The configured source for each > in tempX_label. > > Temperatures are measured in degrees Celsius and measurement resolution is 1 > -degC for temp1 and and 0.5 degC for temp2 and temp3. For temp4 and higher, > -resolution is 1 degC for W83667HG-B and 0.0 degC for NCT6775F and NCT6776F. > +degC for temp1 and and 0.5 degC for temp2 and temp3. For W83667HG-B, temp4 > +has resolution 1 degC. For NCT6775F and NCT6776F, temp4 to temp6 have > +resolution 0.5 degC, while temp7 to temp9 have resolution 1 degC. > An alarm is triggered when the temperature gets higher than high limit; > it stays on until the temperature falls below the hysteresis value. > Alarms are only supported for temp1, temp2, and temp3. > > > -- > Jean Delvare _______________________________________________ lm-sensors mailing list lm-sensors@xxxxxxxxxxxxxx http://lists.lm-sensors.org/mailman/listinfo/lm-sensors