Hello, > + * https://www.renesas.com/in/en/document/mah/rzv2m-users-manual-hardware?language=en I took a look into that now, and there are a few things I noticed. The PWMCYC register description has: To change the setting value of the PWM cycle setting register (PWMm_PWMCYC), set the PWME bit of the PWM control register (PWMm_PWMCTR) to 0b and stop the counter operation. If it is changed during counter operation, PWM output may not be performed correctly. This isn't repected in the driver. Please either fix that or add a comment why you think this is not necessary. If you choose to adhere to that, also note it in the Limitations section that I asked you to add. In .apply() you subtract 1 from the calculated value of PWMCYC. When looking through section 17.4 Function Details I don't see this justified. However in 17.3.2.2 the formula is as you quoted in the driver (i.e. PWMm_PWMCYC = (PWM period (ns) / (PWM_CLK period (ns) × Division ratio)) − 1). Can you maybe test which of the two is correct, maybe adapt the driver code and note in a comment about the difference? Also comment would be nice about the fact that the native polarity of the hardware is inverted (i.e. it starts with the low part). I didn't recheck, maybe the inversion bit handling must be switched? A 100% duty cycle is only possible (according to Figure 17.4-2) with PWMLOW > PWMCYC. Assuming this is correct, there is the problem that the two registers have the same width, so if PWMCYC is 0xffffff a 100% duty isn't possible. So please stick to only using values < 0xffffff for PWMCYC. Best regards Uwe -- Pengutronix e.K. | Uwe Kleine-König | Industrial Linux Solutions | https://www.pengutronix.de/ |