Hi Rob,
Thanks for the review.
On 9/23/20 12:03 PM, Rob Herring wrote:
On Wed, Sep 16, 2020 at 11:22:19PM -0400, Thara Gopinath wrote:
Introduce a new binding parameter to thermal trip point description
to indicate whether the temperature level specified by the trip point
is monitored for a rise or fall in temperature.
Signed-off-by: Thara Gopinath <thara.gopinath@xxxxxxxxxx>
---
.../devicetree/bindings/thermal/thermal-zones.yaml | 7 +++++++
1 file changed, 7 insertions(+)
diff --git a/Documentation/devicetree/bindings/thermal/thermal-zones.yaml b/Documentation/devicetree/bindings/thermal/thermal-zones.yaml
index 3ec9cc87ec50..cc1332ad6c16 100644
--- a/Documentation/devicetree/bindings/thermal/thermal-zones.yaml
+++ b/Documentation/devicetree/bindings/thermal/thermal-zones.yaml
@@ -161,6 +161,13 @@ patternProperties:
The active trip type can be used to control other HW to
help in cooling e.g. fans can be sped up or slowed down
+ monitor-falling:
+ description: |
+ boolean, If true, the trip point is being monitored for
+ falling temperature. If false/absent/default, the trip
+ point is being monitored for rising temperature.
+ type: boolean
What if you wanted to monitor for both?
You usually don't want to. At really low temperature trip (5 degree C or
0 degree C) you care about starting to monitor when the temperature
falls below the trip. At high temp trip points, you care about starting
to monitor when the temperature rises above the trip point. The thermal
framework takes care of stopping the monitoring (dependent on type of
monitoring, hysteresis etc.)
+
required:
- temperature
- hysteresis
--
2.25.1
--
Warm Regards
Thara